Lost in the Imperial system!!!

For technical tips, questions etc. on all subjects except Engines and Boilers.
User avatar
gondolier88
Full Steam Ahead
Full Steam Ahead
Posts: 290
Joined: Fri Jun 18, 2010 8:54 pm
Boat Name: No Boat Yet

Re: Lost in the Imperial system!!!

Post by gondolier88 »

Hayden,

Yes, your injector will have a nominal 'size', a '1/2" Injector' for example refers to is being 1/2" OD pipework required to pipe it up. Whatever size your injector is will give you your pipe size.

The supply pipe will see boiler pressure or just above, one great thing about injectors is their inability to overpressure, unlike a feed pump.

At 80psi your boiler will be at around 160deg.C.

To work out the safe working pressure of tube use;

P = 2T x t / D

Where T= Wall thickness
P= Working pressure
D internal diameter of tube
t= safe working stress of copper, 25,000psi divided by a safety margin of 8 gives us 3125psi

So for a 1/2" injector and 16swg tube;

P = 2 x 0.064 = .128
x 3125 = 400
/ .372 = 1075psi

This is, of course, at cold- as copper's strength decreases proportionally to it's working temperature, then it's maximum working pressure is going to be lower, but as we have already used a safety factor of 8, and as 1075psi is 13 times the maximum pressure of your application, then 1/2" 16swg tube would be suitable for you.