fredrosse wrote:The relief valve needs its own connection, with nothing else on that line. The relief valve should be connected as short as possible to the PV. Definite rules for the setup.
I can move the safety to directly off the forged cross, but that's as close as I can get.
fredrosse wrote:I would recommend the vent cock be opened far less than the video shows, and I would recommend a much smaller charging connection.
The charging was restricted to 1/4 sched 80 NPT, which is 0.302". It's that first fill that you have to be slower with. When the PV is hot it's not also acting as a condensor and was happier. The venting, well I was learning.
fredrosse wrote:How high in charging pressure did this test go?
I did several fills up to and not exceeding 150PSI Boiler pressure and tested that the Aquatrol ASME 125PSI Set Valve operated correctly, which it did at 125PSI.
The PV didn't do the water hammer bouncing again.
fredrosse wrote:Seems like much steam leakage going on after you shut the cock, is that so?
Yes. This was not the PV. That 1/4" braided ss hose occured previous physical damage and was leaking steam. It is junk, I will cut it in half so I don't use it again.
-CB