Ball Valve Open/Flow Relationship
- cyberbadger
- Full Steam Ahead
- Posts: 1123
- Joined: Thu Nov 07, 2013 9:16 pm
- Boat Name: SL Nyitra
- Location: Northeast Ohio, USA
Ball Valve Open/Flow Relationship
I'm trying to better characterize a steam ball valve for a little project.
1) What is A?
2) What is B?
3) Is the line in area C linear?
4) Should the Y axis be 'Flow' rather then 'Percent Open' to see the quirkiness of the ball valve?
It's a standard 1/4 turn steam rated Apollo Ball Valve (Shouldn't really matter).
-CB
1) What is A?
2) What is B?
3) Is the line in area C linear?
4) Should the Y axis be 'Flow' rather then 'Percent Open' to see the quirkiness of the ball valve?
It's a standard 1/4 turn steam rated Apollo Ball Valve (Shouldn't really matter).
-CB
- barts
- Full Steam Ahead
- Posts: 1070
- Joined: Wed Nov 18, 2009 6:08 am
- Boat Name: Otter, Rainbow
- Location: Lopez Island, WA and sometimes Menlo Park, CA
- Contact:
Re: Ball Valve Open/Flow Relationship
-------
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
-
- Full Steam Ahead
- Posts: 186
- Joined: Sun Sep 02, 2012 2:39 pm
- Boat Name: No Boat Yet
- Location: Cathlamet, WA
Re: Ball Valve Open/Flow Relationship
The way you have it is what appears to be common practice with the stem position on the bottom.
That said, a ball valve is a little under 20% open at 45deg and is not 50% open until around 67.5deg
Good steaming
Dave
That said, a ball valve is a little under 20% open at 45deg and is not 50% open until around 67.5deg
Good steaming
Dave
- cyberbadger
- Full Steam Ahead
- Posts: 1123
- Joined: Thu Nov 07, 2013 9:16 pm
- Boat Name: SL Nyitra
- Location: Northeast Ohio, USA
Re: Ball Valve Open/Flow Relationship
Thanks guys!
-CB
-CB
-
- Full Steam Ahead
- Posts: 186
- Joined: Sun Sep 02, 2012 2:39 pm
- Boat Name: No Boat Yet
- Location: Cathlamet, WA
Re: Ball Valve Open/Flow Relationship
FYI: When I say percent open that is percent of the fully open valve area not neccessarily the flow which may vary some depending on the characteristics of the fluid in being moved.
Dave
Dave
- barts
- Full Steam Ahead
- Posts: 1070
- Joined: Wed Nov 18, 2009 6:08 am
- Boat Name: Otter, Rainbow
- Location: Lopez Island, WA and sometimes Menlo Park, CA
- Contact:
Re: Ball Valve Open/Flow Relationship
In case some translation is needed:
the X axis means either Kv or Cv as a percentage of their maximum
values.
Here's a discussion of how to use Cv in calculations:
http://www.engineeringtoolbox.com/flow- ... d_277.html
- Bart
Valve flow is typically described by Cv in US units; in the graph abovethe X axis means either Kv or Cv as a percentage of their maximum
values.
Here's a discussion of how to use Cv in calculations:
http://www.engineeringtoolbox.com/flow- ... d_277.html
- Bart
-------
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
- fredrosse
- Full Steam Ahead
- Posts: 1906
- Joined: Fri Nov 20, 2009 5:34 am
- Boat Name: Margaret S.
- Location: Phila PA USA
- Contact:
Re: Ball Valve Open/Flow Relationship
The chart of ball valve flow coefficient vs valve opening is only half the story. The fluid system to which the valve is connected has a strong influence on the flow rate, and the charts presented show only the valve characteristic.
As an extreme example, say you have a pressurized tank with just the valve connected, and compare this to the same condition, except there is 1mile of pipe added to the circuit. In the first case the valve opening governs the flow, and from zero opening to full opening flow will generally increase continuously.
In the second case, the friction in the one mile of pipe dominates the flow, and limits the flow to a small percentage of the first case. As the valve is opened to, say 10%, most of the flow is established, and limited by the one mile pipe friction. Further opening of the valve results in no increase of flow. While this is an extreme example, I have seen many instances where line friction, in the form of a clogged strainer, or an undersized pipe, or other restriction within the circuit is the relevant parameter of the flow rate. In all fluid systems the circuit has an influence that reduced the influence of the valve, except for full shutoff.
As an extreme example, say you have a pressurized tank with just the valve connected, and compare this to the same condition, except there is 1mile of pipe added to the circuit. In the first case the valve opening governs the flow, and from zero opening to full opening flow will generally increase continuously.
In the second case, the friction in the one mile of pipe dominates the flow, and limits the flow to a small percentage of the first case. As the valve is opened to, say 10%, most of the flow is established, and limited by the one mile pipe friction. Further opening of the valve results in no increase of flow. While this is an extreme example, I have seen many instances where line friction, in the form of a clogged strainer, or an undersized pipe, or other restriction within the circuit is the relevant parameter of the flow rate. In all fluid systems the circuit has an influence that reduced the influence of the valve, except for full shutoff.
- cyberbadger
- Full Steam Ahead
- Posts: 1123
- Joined: Thu Nov 07, 2013 9:16 pm
- Boat Name: SL Nyitra
- Location: Northeast Ohio, USA
Re: Ball Valve Open/Flow Relationship
I don't especially like black boxes myself.fredrosse wrote:The chart of ball valve flow coefficient vs valve opening is only half the story.
For my application, as it exists.
Boiler Nozzel -> 1/2" Schedule 80 seamless steel pipe -> Ballvalve(Used Isolation on/off) -> 1/2" Steam King Hose -> same kind of pipe -> Ballvalve(Flow - ie one I'm characterizing) -> same kind of pipe -> 1902 Toledo Engine(1/2" NPT inlet).
It's 8-10FT length including the hose.
So no strainers, and despite a restriction in the steam King Hose ID the max flow is sufficient for my project.
-CB
- barts
- Full Steam Ahead
- Posts: 1070
- Joined: Wed Nov 18, 2009 6:08 am
- Boat Name: Otter, Rainbow
- Location: Lopez Island, WA and sometimes Menlo Park, CA
- Contact:
Re: Ball Valve Open/Flow Relationship
My experience w/ ball valves as throttle was not great, but that was on a boiler w superheater, so the steam temps could have been high for Teflon.
- Bart
- Bart
-------
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
Bart Smaalders http://smaalders.net/barts Lopez Island, WA
- Lopez Mike
- Full Steam Ahead
- Posts: 1903
- Joined: Wed Dec 07, 2011 6:41 am
- Boat Name: S.L. Spiffy
- Location: Lopez Island, Washington State, USA
Re: Ball Valve Open/Flow Relationship
I get by with a ball valve for my throttle but it is a bit sudden when opening. I haven't researched it but is there any off the shelf 1/4 to 1/2 turn alternative? And I don't mean some wonderful machining project with castings.